Yahoo Answers is shutting down on 4 May 2021 (Eastern Time) and the Yahoo Answers website is now in read-only mode. There will be no changes to other Yahoo properties or services, or your Yahoo account. You can find more information about the Yahoo Answers shutdown and how to download your data on this help page.

How to check if a fuse is good/bad in a live circuit using Multimeter?

Assuming the circuit is live, and we can't pull the fuse out.

4 Answers

Relevance
  • 2 years ago
    Favourite answer

    VERY SIMPLE, APPLY BOTH PROBES ACROSS FUSE,SET METER TO AC VOLT.

    IF NO READING IS SHOWED, FUSE IS GOOD.

    IF SHOWING 120Vac, FUSE IS OPENED.

  • 2 years ago

    If the circuit is Live then the fuse is good. If the circuit is dead then the fuse MAY be bad.

  • 2 years ago

    If you connect a voltmeter across the fuse, it will read zero volts if the fuse is good. Set the meter on a scale higher than the line voltage, as it will see line voltage if blown.

    BUT this is not a guarantee, as if the fuse is open AND there is no load on the circuit, the voltmeter will see an open circuit and, depending on the type of meter, may read zero. An ordinary digital DVM will show a fluctuating voltage near zero as the meter leads pick up atmospheric noise. An analog voltmeter will read zero.

    Another method is to connect the voltmeter between the load side of the fuse and neutral or ground. It will read line voltage if the fuse is good and close to zero if the fuse is bad. This method avoids the possible false reading of the first method.

  • ?
    Lv 7
    2 years ago

    Simple answer: A good fuse will have no Voltage drop

    when it's circuit is loaded.