Yahoo Answers is shutting down on 4 May 2021 (Eastern Time) and the Yahoo Answers website is now in read-only mode. There will be no changes to other Yahoo properties or services, or your Yahoo account. You can find more information about the Yahoo Answers shutdown and how to download your data on this help page.

?
Lv 7
? asked in Science & MathematicsEngineering · 2 years ago

I have to distribute power across and around my land (6.5 ha, 16 acrres)?

Should I use ONE earth point, or can I have a few of them around the perimeter?

3 Answers

Relevance
  • Anonymous
    2 years ago
    Favourite answer

    When covering a large area multiple grounds is a good idea in case one is compromised.

  • 2 years ago

    REAL EARTH GROUNDING POINTS CAN BE AS MANY AS REQUIRED ACCORDING TO YOUR SITUATION, PROVIDED YOU INSTALL AT LEAST 6 FEET THICK COPPER ROD ( ONE INCH DIAMETER ), AND PICK THE INSTALLATION POINT ON WET SOIL.

  • 2 years ago

    How many power points, what power/current, what distance?

    I suspect the distances may be too large for a 220 volt line (assuming Europe) and will require transformers, and thus require a grounding point for each one.

    But if no transformers are involved, one grounding point is ok.

    18 acres, even in a square, involves distances of 800 feet or more. could be twice that at least.

    1000 feet and 10 amps requires a heavy wire...

    allowing 5 volts drop (high), that is 1/2 Ω round trip, 1/4 each.

    #4 wire is 0.25 Ω per 1000 feet, so that would do, but 1000 ft of outdoor rated 4-3 would be very expensive, specially if you had to put it in conduit.

    Consult a local electrician, who would know the local regulations.